Adding a 50A welder receptacle/subpanel?

Caver Dave

Just holdin' it down here in BFV
Moderator
Joined
Mar 10, 2005
Location
Hooterville (24171)
So, our shops PO's brainiac brother ("electrical engineer" 🤣) conned him into a 100AMP FLUSH mount panel.
There are 1 each: 60A (stove), 30A (air compressor), 20A (well pump) double pole breakers and the rest of the slots are full of 20A single pole breakers (lights/receptacles)

After a couple of years of disconnecting the 220V stove plug (of course it's *behind* the fridge), connecting an adapter cable (4-prong to 3-prong) and then unwinding the 35' extension cordage diagonally across the shop... TIRED of tripping over the cord (6/6? Sxxx), tired of it being 6" short of where I need to weld and then undoing to return the stove to service (shop is also our guest quarters/entertaining space) 🤬 ...

Thought adding either another 50A receptacle or a subpanel (near current panel = where I weld), swapping a couple of the SP 20A breakers for piggyback style (to gain space for 50/60A DP breaker) and snake the wires out to a SURFACE mount receptacle/subpanel could be lightyears faster/cheaper than involving a contractor to swap the existing panel to a larger 200A panel?

Doable?
OR is there a better/faster/cheaper alternative?
 
It could possibly trip the main breaker if you had everything going at once but it should be fine. I personally would bring it out of the wall in an LB and run conduit with #6 thhn over to where you want an outlet ( or do a blanking plate over a deep quad box and put a cord grip in the middle do away with the outlet). Buy some 20a mini tandems and double up a few of the lighting circuits, put the 50a breaker in and be done.
 
It could possibly trip the main breaker if you had everything going at once but it should be fine.
I figured that could happen, but would take a perfect storm 🤓
I personally would bring it out of the wall in an LB and run conduit with #6 thhn over to where you want an outlet ( or do a blanking plate over a deep quad box and put a cord grip in the middle do away with the outlet). Buy some 20a mini tandems and double up a few of the lighting circuits, put the 50a breaker in and be done.
Great feedback brother!
Was gonna put the outlet (needed for both welder & plasma) on an outboard stud (bookending the panel) and since I'd need a hole in the drywall (to drill the stud for wire pass-thru from panel cavity), will likely add some horz supports and could flush mount a deep quad box?
 
I was in a similar situation except I didn’t have 220 at all in my shop. I ran 3/4 grey conduit from my main panel into my garage and pulled 6 gauge which terminated into a 6-50R (3-prong receptacle). Last week, I added another receptacle to that same circuit to run my plasma and compressor (combined <40A).

1281564C-7AB6-4EBD-B78B-04BB145188DC.jpeg



I started going down the road of adding a sub panel but that became a lot more work for something I truly didn’t need. Do what works for your needs and keep it simple.
 