Ok, so I get home from work this morning and I have no water. I have 120 volts on both hots at the well head (220 pump). The gound is good as well. So I had the pleasant experience of pulling up the pump. The well is 160' deep with the pump at about 150'. This was heavy as hell to pull by myself, but I got it out. I cut the wires at the splice for the motor. I hooked the motor up at the junction box at the well and it worked. Keep in mind that the motor didn't work with it hooked up to the 150'+ wire running down the pipe. Armed with this knowlege, I continuity checked the wires running down the pipe. Sure enough, one of the hots is "open". Now, replacing the one hot wire won't be a problem, except for the "waterproof" splices. Does anyone know if Home Depot or Lowe's sells this type of heat shrink with the hot glue stuff? Also, I was thinking about this a little more. The pump has a little twist from the torque at startup. The pump is wired with either 12ga. or 10ga. sinlge strand wire. Shouldn't it be multistrand to allow a little more movement over time or is this just a fluke. I don't want to put in single strand if this is going to happen again. BTW, the well is only 2 years old. TIA.
Will.