ANother question, something I have always wondered. My ground, and my common are tied together in my box also. So, what's the difference?
For all practical purposes in a 110/220 single phase residential application there is no difference between the neutral and the ground (i.e. grounding conductor versus grounded conductor for the code junkies) There is no common, that would be in a DC control circuit, but I digress.
Note that the above statement will carry you through anything you need to think through but there are some different installations (installing a secondary sub panel to feed an addition for instance) where the above would not hold true.
If you ever want to re wire the house call me for any add on stuff you will do just assume the ground and neutral are the same.
Ron not sure what you mean about half the house. Both sides of my breaker box are tied together at the top and bottom. All of my 220 outlets feed from the same place, one on top of the other.
I'll skip all the sine wave explanation and say that 220v is a house is derived from one leg being +110V while the other leg is -110V, and thee two legs are perfectly opposite out of phase. This is why if you go to your dryer outlet and use a multi meter you get 110 from either hot to ground but 220 hot to hot.
in order to keep from having transformers in everyones house utilities feed two 110V circuits perfectly opposite phase and the main distribution panel (breaker box) separates them.
There are 2 styles here
1) Is called Pillared or columned separation and is by far the most common.
In this configuration your breaker box is most likely numbered
1 2
3 4
5 6
7 8
9 10
11 12
13 14
15 16
17 18
19 20 etc
and the main breaker is fed by two separate hots and each one feeds a given straight line copper bus that runs down the back of the panel. All the breakers on the left snap to bus "A" and the breakers on the right snap to bus "B" This is said to be A phase and B phase.
the buses are perfectly (ok....again for those who want to argue semantics, nothing is perfectly isolated but practically perfectly) isolated
2) The second arrangement is actually technically superior but more costly to produce and as such has been pretty much eliminated from existance
In that configuration the numbering above *should* look like
1 11
2 12
3 13
4 14
5 15
6 16
7 17
8 18
9 19
10 20
In this case the breaker is still fed from the meter with 2 hots and still feeds two dedicated copper bus bars but now instead of straight lines they look like interlocking letter "E"s such that
1,11,3,13,5,15,7,17,9,19 are "A" phase and 2,12,4,14,6,16,8,18,10,20 are "B" phase.
Now all this is easy enough until I tell you that you can't trust the numbering systems because Cutler hammer and Square D got in the spec war years ago and tried to get each others product speced out as non conforming and as a result each changed their numbering protocol back and forth multiple times.
The above formats should hold true for panels bought today, and again i am taling strictly single phase resi panels.
To determine which panel configuration you have look in the inside cover there should be a simple diagram there.
Since the two bus bars are isolated (A/B) if you plug 110 into a single outlet you will only power half the breakers in the panel. You *could* feed a second 110 into an outlet on the leg and get all your 110 hot, BUT MAKES SURE YOU SWITCH OFF ALL 220v breakers as you will be feeding two legs in phase...