I have a propane generator, 3550 watt with 6.75hp briggs and have a question. Im guessing my 100b tank is located around 20-25 feet away from where I'm installing the generator. The tank is used for gas logs in the house also. The piping used was 3/8" OD copper piping. The regulator on the tank is at low pressure 11" Wc (6 ounces) which is what my generator requires as well as the gas logs. My question now is, will the 3/8" OD piping with a run of around 20-25 (T'd off at 20-25 feet to generator) feet be sufficient to carry the amount of propane needed to power the briggs on the generator? Or would i need to move up past 3/8"OD in size? Im thinking it will be sufficient but since i can't really understand the charts, i was gonna see if someone could explain a little better. Thanks.